MAINS powered clocks correct. I wonder what their correction strategy
Post by VladSpeaking about MAIN... I was interesting to see if "leap second"
event has correlation with MAIN frequency fluctuation
Here is graphs for the MAIN periods recorded. Note: The data on the
charts is "smoothed" by Bezier curves
I could see some "surge" which starts to climb in December 30 and
end at Dec 31 at the time close to the "leap second" event. But not
sharp.
For 16-12-29 00:00 to 17-01-02 00:00
http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png [1]
http://www.patoka.ca/OCXO/60hz-periods-Dec31.png [2]
It will be interesting to see/compare if anybody else has similar stats.
Regards,
Vlad
What modern loads are actually sensitive to high (say, +10 to +20%) line
voltage?
Old incandescent light bulbs were among the most sensitive loads in the
past (so much so, that 130V light bulbs were commonly available from the
industrial suppliers).
I would naively expect the modern CFL's and LED replacements to be fine
with higher line voltage because they have their own built-in
switching
regulation.
A lot of modern electronic equipment with switching supplies, are just fine
at +20% line voltage and may even run cooler.
Tim N3QE
There are a couple of recent threads concerning the power line mains
voltage standards. After a bit of research and thinking, I have found
* The standard in the US for the past 50 years has been 120/240 V +/- 5%
RMS at the service entrance to the building. This is a range of
114/228 V to 126/252 V.
* The load voltage could be as low as 110/220 V and as high as 125/250 V
and be within specifications.
(1) Service voltage: This is the RMS voltage measured at the service
entrance to the building (at the metering point).
(2) Utilization voltage: This is the RMS voltage measured at the load.
It might be measured at an unused socket in a power strip
feeding
several pieces of electronic equipment, for example. There are of
course many different utilization voltages present in a home or
business, depending on where you make the measurement.
Most US homes and small businesses are powered by what is commonly
called a "split-phase" 240 V feed. The final distribution system
transformer has a 240 V center-tapped secondary. The center tap is
grounded, and three wires are fed to the building (actually it might be
(1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L2.
(2) Neutral (white wire) -- This wire is grounded at the
distribution
system and at the service entrance to the building.
(3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L1.
Large appliances and HVAC systems are usually connected across L1-L2
(240 V), while most sockets are on circuits either connected across L1-
neutral (120 V) or L2-neutral (120 V).
The voltages I have described are the current standardized values for
the service voltage which have been in general use for about 50 years
(120/240 V +/- 5%). I believe that the original systems installed before
1940 were designed for a 110/220 V nominal service voltage, but after a
report in 1949 the nominal service voltage was increased to 117/234 V,
as specified in ANSI C84.1-1954. After research in actual buildings, in
the 1960's the nominal service voltage was increased again, to 120/240 V
in the ANSI C84.1-1970 standard. The purpose is to keep the
utilization
voltage at the load above 110/220 V.
The voltage at the service entrance should in most cases be in Range A
(120/240V +/-5%). On each 120V leg the service voltage should
therefore
be between 114 and 126 V. The utilization voltage at the load should be
between 110 and 125 V due to losses in building wiring.
http://www.pge.com/includes/docs/pdfs/mybusiness/ [3]
customerservice/energystatus/powerquality/voltage_tolerance.pdf
These voltage specifications were designed for resistive loads and
measurement of the true RMS voltage. In most electronic equipment built
over the past 50 years, the power supply input circuitry is
basically a
rectifier connected to a smoothing capacitor. This leads to high input
current surges during the peaks of the waveform, so that the peak
voltage is reduced much more by the building wiring resistance than if
the load was resistive for the same power consumption.
So the waveform shape at different utilization locations in a
building
(with active equipment loads) may be different, so the voltage measured
by different AC measuring instruments can differ. Many meters are full
wave average measuring but calibrated so they only read RMS voltage
correctly on pure sinewaves. Other meters are true RMS measuring and
will read very close the correct RMS voltage even if the waveform is
distorted.
--
Bill Byrom N5BB
Post by CIW308 VE6OHMark,
CSA have standards for over and under voltage, Typical no more
that 3%
Post by CIW308 VE6OHover and 5% under if memory serves me.
This might help (
http://www.safetyauthority.ca/sites/default/files/csa- [4]
fia3660-voltagedropcalc.pdf
Post by CIW308 VE6OH)
The power companies here in Alberta are generally good about
fixing
Post by CIW308 VE6OHproblems with line regulation.
There can be problems with industrial areas and big welders or
motors
Post by CIW308 VE6OHstaring as I am sure you know.
I am sure they do not want the bill for replacing equipment that
was
Post by CIW308 VE6OHsubjected to over voltage.
On UPSs: I am sure you are aware that may of them are not TRUE sine wave
so the DMM may not read correctly.
Mitch
_______________________________________________
To unsubscribe, go to https://www.febo.com/cgi-bin/
mailman/listinfo/time-nuts
and follow the instructions there.
_______________________________________________
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts [5]
and follow the instructions there.
V.P.
and follow the instructions there.