How do you measure solar energy flowing one-way to the grid on the AC1
connection of an SW-series inverter? Is there a one-way transducer
available so that the circuit does not have to be opened?

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Jeffrey Wolfe, Global Resources
2001-10-28 22:25:18 UTC
Permalink
I betcha Ethan Brand has something for this. He's able to do an awful lot
with transducers. I'm sure ignoring "negative" flow would not be hard.

Jeff

On Sunday, October 28, 2001 12:06 PM, Joel Davidson
Post by Joel Davidson
How do you measure solar energy flowing one-way to the grid on the AC1
connection of an SW-series inverter? Is there a one-way transducer
available so that the circuit does not have to be opened?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Peter Talmage
2001-10-28 22:30:15 UTC
Permalink
Dear Joel,

We use standard Kwhr meters with detents that allow
flow in one direction only. A Brand meter will do the
same if you "plug" the meter into the AC1 output and
put the grid on the meter load side. (for up to 1850
watts.)

Yours, Peter Talmage
Post by Joel Davidson
How do you measure solar energy flowing one-way to
the grid on the AC1
connection of an SW-series inverter? Is there a
one-way transducer
available so that the circuit does not have to be
opened?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-29 01:31:19 UTC
Permalink
Nice ideas. The detents are a good way to go for new installations. Ethan
Brand also suggested putting his meter in line, but I have over 1850
watts. Also, a one-way transducer on other people's existing systems would
allow us to see how the systems are performing. Any other thoughts?
Post by Peter Talmage
Dear Joel,
We use standard Kwhr meters with detents that allow
flow in one direction only. A Brand meter will do the
same if you "plug" the meter into the AC1 output and
put the grid on the meter load side. (for up to 1850
watts.)
Yours, Peter Talmage
Post by Joel Davidson
How do you measure solar energy flowing one-way to
the grid on the AC1
connection of an SW-series inverter? Is there a
one-way transducer
available so that the circuit does not have to be
opened?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-29 01:31:19 UTC
Permalink
Nice ideas. The detents are a good way to go for new installations. Ethan
Brand also suggested putting his meter in line, but I have over 1850
watts. Also, a one-way transducer on other people's existing systems would
allow us to see how the systems are performing. Any other thoughts?
Post by Peter Talmage
Dear Joel,
We use standard Kwhr meters with detents that allow
flow in one direction only. A Brand meter will do the
same if you "plug" the meter into the AC1 output and
put the grid on the meter load side. (for up to 1850
watts.)
Yours, Peter Talmage
Post by Joel Davidson
How do you measure solar energy flowing one-way to
the grid on the AC1
connection of an SW-series inverter? Is there a
one-way transducer
available so that the circuit does not have to be
opened?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Doug Pratt
2001-10-29 03:40:47 UTC
Permalink
A high-end solution is Ethan Brand's "One Meter", for those that want to
send data to their PC or other data logger. He uses a single AC
transducer, the AC1 input/output wire goes thru in one direction, the AC
output wire goes thru in the opposite direction, so any grid power that
passes thru the inverter to support loads on the AC output terminal gets
automatically zeroed out. This is an $800 solution, but it will monitor
all DC and AC power flow, and send all the info to your handy-dandy
spreadsheet. I encouraged Ethan to develop a package that would monitor
power in and out of the SW or any other intertied, battery-based system,
this is what we came up with. I've ordered a couple of them, and will be
installing one on my son-in-law's 7kW system (when it arrives). I'll let
the list know how it works out.
Doug Pratt
Dear Joel,

We use standard Kwhr meters with detents that allow
flow in one direction only. A Brand meter will do the
same if you "plug" the meter into the AC1 output and
put the grid on the meter load side. (for up to 1850
watts.)

Yours, Peter Talmage
Post by Joel Davidson
How do you measure solar energy flowing one-way to
the grid on the AC1
connection of an SW-series inverter? Is there a
one-way transducer
available so that the circuit does not have to be
opened?
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Peter Talmage
2001-10-29 12:39:16 UTC
Permalink
Dear Joel,

Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.

Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-29 15:34:19 UTC
Permalink
I just talked with Ethan. He said put one transducer on both AC1 and AC2
to read PV production :-)
Post by Peter Talmage
Dear Joel,
Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.
Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-29 15:34:19 UTC
Permalink
I just talked with Ethan. He said put one transducer on both AC1 and AC2
to read PV production :-)
Post by Peter Talmage
Dear Joel,
Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.
Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Doug Pratt
2001-10-30 02:35:24 UTC
Permalink
Joel,
I'm pretty sure Ethan said (or meant to say) "one transducer on both
AC1 and AC output to read PV production." AC2 is for generators, it's
input only.
-Doug

-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Monday, October 29, 2001 7:34 AM
To: RE-wrenches at topica.com
Subject: Re: Measuring PV kWh on net metered systems [RE-wrenches]

I just talked with Ethan. He said put one transducer on both AC1 and AC2
to read PV production :-)
Post by Peter Talmage
Dear Joel,
Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.
Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-30 05:36:07 UTC
Permalink
Doug,
You and Ethan are correct. The transducer goes on both AC HOT IN 1 and AC
HOT OUT. Do people still use generators that consume non-renewable natural
resources and exhaust toxic gases into the atmosphere?
- Joel
Post by Doug Pratt
Joel,
I'm pretty sure Ethan said (or meant to say) "one transducer on both
AC1 and AC output to read PV production." AC2 is for generators, it's
input only.
-Doug
-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Monday, October 29, 2001 7:34 AM
To: RE-wrenches at topica.com
Subject: Re: Measuring PV kWh on net metered systems [RE-wrenches]
I just talked with Ethan. He said put one transducer on both AC1 and AC2
to read PV production :-)
Post by Peter Talmage
Dear Joel,
Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.
Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-30 05:36:07 UTC
Permalink
Doug,
You and Ethan are correct. The transducer goes on both AC HOT IN 1 and AC
HOT OUT. Do people still use generators that consume non-renewable natural
resources and exhaust toxic gases into the atmosphere?
- Joel
Post by Doug Pratt
Joel,
I'm pretty sure Ethan said (or meant to say) "one transducer on both
AC1 and AC output to read PV production." AC2 is for generators, it's
input only.
-Doug
-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Monday, October 29, 2001 7:34 AM
To: RE-wrenches at topica.com
Subject: Re: Measuring PV kWh on net metered systems [RE-wrenches]
I just talked with Ethan. He said put one transducer on both AC1 and AC2
to read PV production :-)
Post by Peter Talmage
Dear Joel,
Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.
Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Joel Davidson
2001-10-28 17:05:35 UTC
Permalink
How do you measure solar energy flowing one-way to the grid on the AC1
connection of an SW-series inverter? Is there a one-way transducer
available so that the circuit does not have to be opened?

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Jeffrey Wolfe, Global Resources
2001-10-28 22:25:18 UTC
Permalink
I betcha Ethan Brand has something for this. He's able to do an awful lot
with transducers. I'm sure ignoring "negative" flow would not be hard.

Jeff

On Sunday, October 28, 2001 12:06 PM, Joel Davidson
Post by Joel Davidson
How do you measure solar energy flowing one-way to the grid on the AC1
connection of an SW-series inverter? Is there a one-way transducer
available so that the circuit does not have to be opened?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Peter Talmage
2001-10-28 22:30:15 UTC
Permalink
Dear Joel,

We use standard Kwhr meters with detents that allow
flow in one direction only. A Brand meter will do the
same if you "plug" the meter into the AC1 output and
put the grid on the meter load side. (for up to 1850
watts.)

Yours, Peter Talmage
Post by Joel Davidson
How do you measure solar energy flowing one-way to
the grid on the AC1
connection of an SW-series inverter? Is there a
one-way transducer
available so that the circuit does not have to be
opened?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Doug Pratt
2001-10-29 03:40:47 UTC
Permalink
A high-end solution is Ethan Brand's "One Meter", for those that want to
send data to their PC or other data logger. He uses a single AC
transducer, the AC1 input/output wire goes thru in one direction, the AC
output wire goes thru in the opposite direction, so any grid power that
passes thru the inverter to support loads on the AC output terminal gets
automatically zeroed out. This is an $800 solution, but it will monitor
all DC and AC power flow, and send all the info to your handy-dandy
spreadsheet. I encouraged Ethan to develop a package that would monitor
power in and out of the SW or any other intertied, battery-based system,
this is what we came up with. I've ordered a couple of them, and will be
installing one on my son-in-law's 7kW system (when it arrives). I'll let
the list know how it works out.
Doug Pratt
Dear Joel,

We use standard Kwhr meters with detents that allow
flow in one direction only. A Brand meter will do the
same if you "plug" the meter into the AC1 output and
put the grid on the meter load side. (for up to 1850
watts.)

Yours, Peter Talmage
Post by Joel Davidson
How do you measure solar energy flowing one-way to
the grid on the AC1
connection of an SW-series inverter? Is there a
one-way transducer
available so that the circuit does not have to be
opened?
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Peter Talmage
2001-10-29 12:39:16 UTC
Permalink
Dear Joel,

Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.

Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
__________________________________________________
Do You Yahoo!?
Make a great connection at Yahoo! Personals.
http://personals.yahoo.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Doug Pratt
2001-10-30 02:35:24 UTC
Permalink
Joel,
I'm pretty sure Ethan said (or meant to say) "one transducer on both
AC1 and AC output to read PV production." AC2 is for generators, it's
input only.
-Doug

-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Monday, October 29, 2001 7:34 AM
To: RE-wrenches at topica.com
Subject: Re: Measuring PV kWh on net metered systems [RE-wrenches]

I just talked with Ethan. He said put one transducer on both AC1 and AC2
to read PV production :-)
Post by Peter Talmage
Dear Joel,
Ethan offers his meter in a 4 Kw vesion (if that is
enough) with an external current transducer. You will
have toask him if it is one way only as I haven't used
one that way yet.
Yours, Peter
Post by Joel Davidson
Nice ideas. The detents are a good way to go for new
installations. Ethan
Brand also suggested putting his meter in line, but
I have over 1850
watts. Also, a one-way transducer on other people's
existing systems would
allow us to see how the systems are performing. Any
other thoughts?
- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
Loading...