Post by JNugentBut installing a non-compliant socket in the UK is a breach of the IEE
regulations (or whatever those regs are now called).
See:
"The Regulation you need to have a look at is 553-01-03 which refers
to Table 55A that lists BS 546 plugs/sockets but not the Schuko Socket
Outlets (16A) to IEC884 you refer to. However, as a designer, you may
wish to note Regulations 120-01-03 and 120-02-01 that allow you to
make a special consideration with respect to the degree of safety of
the installation being not less than obtained by compliance with the
Regulations and if so, recording this as a departure on your
Electrical Installation Certificate."
and:
"You also need to ensure compliance with The Plugs and Sockets etc.
(Safety) Regulations 1994. These require sockets for use with
"Standard" plugs (i.e. BS 1363 plugs) to themselves be to BS
1363-2:1995 13 A plugs, socket-outlets and adaptors Specification for
13 A switched and unswitched socket-outlets.
However, the regulations also state the following with regard ro
standards of other European states.
'...such requirement shall be satisfied if the electrical device
conforms to any standard or specification recognised for use in a
member State, provided that conformity to such a standard or
specification provides a level of safety equivalent to that which
would be provided by conformity to the relevant British Standard, and
any reference to such a requirement shall be construed accordingly.'
The use of IEC 884 sockets therefore seems OK. "
and:
"Be aware that any circuit with an unfused plug/socket (schucko or
older British) needs to be backed up by a 16A MCB or a 13A fuse.
Direct connection to a UK ring final circuit, normally wired in 2.5mm,
and backed by a 32A MCB or 30A hot wire fuse, is not accepeted. I have
put Schucko socket in my new shower room on a dedicated 16A RCBO
radial, and another one on a 13A fused spur. I have the building
control office paperwork to say its acceptable to them. They did want
my paperwork in English, oddly enough, though I had given them the
option of test results in German."
https://www.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=11857
Post by JNugentBut neither are "banned" in the everyday sense of that word.
Exactly. See above.
Post by JNugentAnyone may
own them as long as they are only used in compliance with the regs and
the law. And for the socket, that means not used at all (except perhaps
as a trailing socket arrangement with a 13A plug on the other end, as an
adaptor).
Not true. See above from IET (The Institution of Engineering and
Technology) website.
MM